Hi Stephan,
Here are a few comments on your plot:
Following error seems fairly high at ~ 100 counts (although you haven't included the
resolution of your system).
Friction/Stiction seems very high. At the end of a move the output remains high (100 counts) but there is no motion. It appears to take an output of over 150 before any motion occurs.
The I gain of
0.2 seems very high. Typical values are usually 0.001 ~ 0.1. But you have a Max Integrator Limit of 50 counts. The result is that the integrator quickly applies 50 counts and then saturates without enough range to achieve any motion and drive the error to zero.
Message: 6221 |
Date: 12/4/2012 |
Subject: Re: Backrunning after Jog |
thanks a lot for your comments! You are completly right! The
friction is very high, thats because a large linear guide (i hope
this the right name) is driven by a small motor. But for testing
and learning its good enough, i think.
What do you mean with " although you
haven't included the resolution of your system" ?
I suppose i have overlooked one detail!
Thanks a lot!
Stefan
Stefan Polatzky, Mechanische Systeme,
Leitenweg 8, 83543 Rott am Inn, Mobil: 0172/8477872,
Tel/Fax: 08039/908297, waxmatch@...
Am 04.12.2012 19:44, schrieb Tom Kerekes:
Hi Stephan,
Here are a few
haven't included the resolution of your system).
Friction/Stiction
The I gain of
Message: 6222 |
Date: 12/4/2012 |
Hi Stefan, I was referring to the counts/inch of your system. Depending on your encoder resolution, gear ratios, lead screw pitch and so forth one encoder count will correspond to some linear distance on your table. If you don't tell us this we don't know if an error of 100 counts is 0.1 inches or 0.001inches. In KMotionCNC you set the resolution in Tool Setup | Trajectory Planner | Axis Parameters | cnts/inch Regards TK
Message: 6223 |
Date: 12/4/2012 |
i thought i´ve something forgot to adjust but it was only to tell
you! Sorry!
I have adjusted a resolution of 101600 counts/inch to move the
right distance
So a fault of 100 counts are roughly 1e-5 inches.
That brings me to another question:
Why the resolution i have to adjust, is 4 times higher then the
real one?
Is there a 4 times evaluation per count in the controller?
For example:
I have a encoder with 4000 counts/rev and a leadscrew pitch of
0.157480 inches ( 4mm ), so i have a real resolution of 25400
counts/inch.
25400 *4 counts/inch = 101600 counts/inch is what i have to
adjust, as i described above.
Thanks a lot for your patience!
Best Regards,
Stefan
Am 04.12.2012 20:46, schrieb Tom Kerekes:
Hi Stefan,
Message: 6224 |
Date: 12/4/2012 |
Hi Stefan, There is often confusion between encoder lines (or cycles) per rev vs encoder quadrature counts. One line on an encoder generates 4 quadrature transitions of the A B signals. It often amazes me that encoder manufactures often spec an encoder as 1000cpr with there being no way to be sure whether they mean cycles or counts. Most of the time they mean cycles. Regards TK
Message: 6225 |
Date: 12/4/2012 |
your support only was it worth to buy the controller!
Thanks and have a nice Day.
Best Regards
Stefan
Am 04.12.2012 22:27, schrieb Tom Kerekes:
Hi Stefan,